My son just bought an old Charmilles D10 sinker EDM, a 3KW machine
He's in a residential area with no 3-Phase running to his shops. 120A service panels.
Guys on some forums are saying it "requires a rotary phase converter" while I'm suggesting a cheap VFD
Does anyone here know of situations where a VFD WILL NOT WORK to replace an old school phase converter?
At this point the VFDs have dropped in price enough to be less expensive than a RPC and a lot more efficient.
Even if you never use the Variable function it produces a 'cleaner' 3-phase voltage set than all but the largest rotaries
running a far smaller load.
What voltage is the sinker motor set up for?
You will need to use the numbers off the motor itslef to set up whatever solution you end up with.
Make sure the setup is large enough even if you never approach the actual motor rating in use.
The motor will start better (faster) and run smoother with a converter that is larger than the minimum required.
Article 430 covers motors.
430.122 covers the VFD feed requirements.
NEC sections 215.2(A)(1), 220.40, 220.50, 220.12(C), 430.24, and 409.20 may be useful.
Good luck.
Especially if you get things inspected.
Many residential code officials have very limited experience and training in industrial type equipment connection.
I have met more than a few that had no real knowledge of how Article 430 and motor feeds and breakers are sized and selected.
The normal rather strict pairing of breaker size and conductor size are NOT the same as for 'general use' branch circuits.
Plenty of them barely understand the correct installation of Hermetic Compressor feed (think residential central A/C).
Induction motors and their controller equipment are designed to prevent overloading of feeders and overheating of the motor.
The breakers are solely for short circuit protection of the feeder to the motor controller.